150V 45A MPPT - roll your own


Author Message
kentfielddude
Senior Member

Joined: 09/05/2019
Location: United States
Posts: 121
Posted: 04:01am 17 Sep 2026      

  SYM-1 said  How many turns are you using on  the 6  KS-520-060A?


I'm planning to use a 2 KS-520-060A.

KS-520-060A( MS-520060-2) is $10.40 piece

KS-521-060A (MS-521060-2) is $13.50 a piece

If I had know the seller had the KS-521 I would have ordered those instead.

I guess the differences between them isn't as much as I thought. KS-520 needs 5 more turns and the performance is very simmilar.



KS-520-060A
37 turns
13 AWG, 16 strands
220uh at 50 amps

9w copper loss
2W core loss

KS-521-060A
32 turns
13awg, 16 strands
Core loss 2w
copper loss 8W



With the KS-520-060A if I increase frequency to 40khz I only need like 110Uh at 50 amps. Which would mean I need 25 turns instead of 37. The switching losses double anyways. It's all a balancing game. An extra 5-20w in switching loss is only like 0.5% out of a 2500w output.