Playing about with a 5kW Hybrid in the shed ATM. Have 6 250W panels connected in the yard; 9 more stacked against the fence. Just wondering how best to treat the batteries I have attached to it. ATM I've got 12 Panasonic LC-P1220P's connected to provide 48V. Not a real lot of capacity to do anything with, so wondering how deep I should cycle them. Just down to 75%, or not even that low? Batteries are all used; from a set of 3kV UPS's that all get a routine battery change every 2 years. They would have all went into service at about the same date, give or take a few days. 12 @ 20Ah would be 2.88kWh storage at the 20h rate, but it's probably more realistic to look at the 3 hour rating which is 15Ah. Found this data sheet. Phil. 2017-12-25_074042_Panasonic_LC-P1220P.pdf |
||||
M Del Senior Member ![]() Joined: 09/04/2012 Location: AustraliaPosts: 155 |
3 strings will give 45-60ah, so good for LED lights and some form of intermittent stereo system/radio use overnight I would say. 10-15ah overnight or 5-10ah for 3 hours early evening. Both useages draw the batteried down to about about 80% capacity. These sort of batteries are designed for long float times and heavy short term draw to power the UPS units, daily use may or may not effect them. ![]() Time will tell. Will you using an inverter for 240v (inverter loss) or a voltage reducer for 12v gear (again a small loss). There are many good 240v LED lights that draw 3w, I use them in my house. Also a good range of 12v lights and radios etc. Mark |
||||
![]() |
![]() |