Jaffasoft Senior Member Joined: 03/11/2010 Location: AustraliaPosts: 102
Posted: 02:24pm 01 Aug 2017
Copy link to clipboard
Print this post
Getting a strange error and no charging going ot the battery from my Morningstar Tristar Inverter.
I spent three days parked under the shade and noticed a positive connection was badly eaten away, so I disconnected the line cut it back a bit up the line and connected it fresh to the positive battery terminal again.
The battery is on 11.9 at the moment. They are two 6V T105 Deep Cycle Trojan Batteries connected to make 12Volts.
The inverter is TriStar Solar Controller TS-45. The error it's flashing is a yellow light on full time and alternating a green and then red light continuously.
This error in the manual says it is a short circuit in the system and to disconnect everything and connect up again. Well, I did that couple times, i have disconnected the positive line and negative line coming from the solar panels directly and also the positive and negative line to the controller completely and see the light all go out so all power and connection are totally disconnected.
It's a stand alone solar panel and battery, controller system in a campervan with 400 watts on the roof. It's been going great for 5 years. Just not sure why it's kicking in and charging again!
At the moment I connected jump lead to the Tragon Bank to top it up idol the van a while to give the battery a boost from the Vans start battery. Just for this day or two as i try to find this short circuit problem.
Any tips on how to trouble shoot? I've got a multi-meter here and checked over the connection lines as best I can all seem in tacked as normal. There is something wrong somewhere because it's still not charging.
Jaffasoft Senior Member Joined: 03/11/2010 Location: AustraliaPosts: 102
Posted: 02:57pm 01 Aug 2017
Copy link to clipboard
Print this post
I discovered two tiny temperature sense wires that have rubber together between the metal battery holder and the plastic battery and were frayed through to wire on both lines it must have been shorting. So the positive line I repaired wasn't frayed that bad that it needed repairing nor was it the cause of the fault I think but I fixed it anyway.
Lights are on full RED/YELLOW manual says that's 0-30% State Of Charge and the meter is back up at 12.7. With 12V fridge running and investor.
So may have solved my own question and will monitor see how it goes next day or two. I have disconnected the heat sensor as I am in moderate to warm climate now! And don't need the extra voltage to charge in at and can repair this in any colder climate I may encounter later. I also reconnected the - + sense wires which had come loose off the battery. Perhaps that made it up and running again too as I repaired that at the same time!?
It's amazing how some tiny thing can bring the entire system down from time to time. Edited by Jaffasoft 2017-08-03
yahoo2 Guru Joined: 05/04/2011 Location: AustraliaPosts: 1166
Posted: 05:28pm 01 Aug 2017
Copy link to clipboard
Print this post
Yes you have found it! the error code is red/yellow---green/yellow
that is either faulty remote temp sense or remote voltage sense. I'm confused, no wait... maybe I'm not...
Jaffasoft Senior Member Joined: 03/11/2010 Location: AustraliaPosts: 102
Posted: 06:10pm 01 Aug 2017
Copy link to clipboard
Print this post
Yes... by now it's up on float at 13.1 so it must be right again. Both the remote temp sense wires were rubbed through to bare wire touching each other along a few centimeters. It been tucked away along side the case rubbing on the battery in the case for four years or so to get to that point. Since 11/2013.