KeepIS

Guru

Joined: 13/10/2014
Location: Australia
Posts: 2062
Posted: 05:39am 10 Sep 2025
Copy link to clipboard 
Print this post

Since having the Fuse boxes updated and the correct Generator (Inverter) feed cable installed, and still running our larger 3.6kW Water heater, I decided to power our Dual oven and 6 zone Bosh Ceramic Hot plate from the Inverter as well. We were using a smaller desktop oven / air fryer up until now.

That means the only thing now on mains is a 15 year old Solar Feed-In Inverter with a 2.8kW array, in other words, it's all feed-in with ZERO mains consumption.

The good thing about the Bosh bench top is that it time slices multiple hot plates, so average load is not additive, and the Dual Oven draws less than I had anticipated.

The result is that we occasionally see loads of around 13kW, but it could be more if the washing machine was on a Hot wash and set to dry the load when the wash cycle was over, but again, I would have to have virtually everything running.

Now this is only a problem for the Battery bank at night, and so far I've still had over 50% charge left in the morning, the Inverter has absolutely no problem, not even a single light flicker with big loads cycling on and off.

Obviously if the weather was bad we would be very mindful of power usage, but at the moment we are operating as though we are on Mains, room lights left on (wife), ceramic heaters in bathrooms (it's winter) and a couple of air conditioners, one running all night on really cold nights, 6 security lights and ambient lights in the back yard, in other words, just pigging out on power usage and still not running the Batteries down

BTW We also run a lot of large wood working machinery in our workshop from morning to dusk most days of the week, including equipment drawing 23kW on startup, mostly large induction motors, one big Induction motor has NO startup cap, just a run cap spinning up a massive steel fan impeller.
_
Edited 2025-09-11 08:25 by KeepIS
NANO:Inverter V 8.2ksLinux AvrDude GUI script V3.3
 
KeepIS

Guru

Joined: 13/10/2014
Location: Australia
Posts: 2062
Posted: 01:16am 11 Sep 2025
Copy link to clipboard 
Print this post

FYI a quick screen photo of the Ceramic Cook Top and other general loads.
Blue:   Inverter Input current.
Green:  Battery Charge current.
Cyan:   Battery Voltage.
RED:    Battery Discharge current.
Yellow: Solar Current.  

Horz scale in minutes updated every second.
Vert scale in Amperes, and in Volts for Cyan trace (Battery Voltage)  

Because of the single Vertical scale, these reading are slightly low. IE: Battery volts is actually 54V.

Below: DC current from Cook-Top cycling from 4.2kW to almost 10kW.



Below: Cycling from 640W <-> 5.4kW and then 640W <-> 3kW.



Below: The Inverter output Wall power Box, the Tesla kWh meter will accurately calculate Power down to very low power levels (PF does not suddenly go to .58 because of the inability of these colour multi function meters to calculate low Power PF.
 
The "INV AC Direct" switch was for emergency running with just essential devices, I have a feeling this may not be needed, but I have it just in case. These meters were reset recently when the new power box was fitted.


_
Edited 2025-09-11 13:09 by KeepIS
NANO:Inverter V 8.2ksLinux AvrDude GUI script V3.3
 
Revlac

Guru

Joined: 31/12/2016
Location: Australia
Posts: 1219
Posted: 12:21pm 11 Sep 2025
Copy link to clipboard 
Print this post

All going very well, Are you going to be beside the grid, (keep the connection) or go full offgrid (as in removal of the lines and meter) later...
I don't have a decent stove yet, that may be something for later.
Cheers Aaron
Off The Grid
 
KeepIS

Guru

Joined: 13/10/2014
Location: Australia
Posts: 2062
Posted: 11:09pm 11 Sep 2025
Copy link to clipboard 
Print this post

Keeping the grid until the 15 year old high In-feed tariffs are shut down in 2028, the In feed connection pays for itself covering infrastructure fees and the credit is also paying for the off-grid system I've built.

I hear they are intending to count any Solar In-feed payments as income, don't have a  time frame, and of course charge you for any In-Feed at certian times to pay for them having to install Batteries reserves due to the amount of home Solar feeding the Grid at certian times of the day.

I found out that I can suspend the Mains for 12 months or so without going through a new connection inspection. At this stage the plan is to drop the mains connection as soon as they start charging us or forcing a smart meter, then remove the old In-feed system and replace the panels to add another 5 or 6kW to the Off-grid system.

This morning at 5.30AM I had over 70% state of charge, it's now 8.45 AM and despite early morning loads of 5 to 9kW the SOC is now at 85%, and I'm only charging the Banks to around 95% these days.

I'm amazed at these batteries, some are coming up to 5 years old, Fake EVE Cells, badly assembled (commercial batteries) and were abused by running fully charged for long periods of time etc, a few years back I stripped them and rebuilt the recovered Cells correctly as nominal 48v units.
_
Edited 2025-09-12 10:43 by KeepIS
NANO:Inverter V 8.2ksLinux AvrDude GUI script V3.3
 
KeepIS

Guru

Joined: 13/10/2014
Location: Australia
Posts: 2062
Posted: 10:49pm 12 Sep 2025
Copy link to clipboard 
Print this post

Overcast morning, at 7.18am screen shot of the Inverter peaking at 10.5kW, batteries at 73% SOC after overnight usage. It's now 8.07am, still overcast and solar output is at 3.7kW and rising. Lucky to be living in a good Solar location like QLD.


NANO:Inverter V 8.2ksLinux AvrDude GUI script V3.3
 
KeepIS

Guru

Joined: 13/10/2014
Location: Australia
Posts: 2062
Posted: 12:33am 14 Sep 2025
Copy link to clipboard 
Print this post

The power level of 10.5kW in the last post is wrong, it's actually much higher.

It's being clipped by the Maximum ADC input voltage of the ARM7. I built this 9" touch screen Solar monitor and coded it years ago. Just checking the circuit and code, there is a resistive divider on the input to keep the 500A Sensor voltage in range, it clamps the ADC input keeping the current to a very low value on overload and clamped at around 3.2V.

I need to modify that ADC input circuit and Code (resistive multiplier value) to read to at least 500A @ 3.2V in order to display the correct switching DC currents to match commercial Current Clamp meters, the down side is this makes very low current readings [< 8A] slightly inaccurate.
NANO:Inverter V 8.2ksLinux AvrDude GUI script V3.3
 
phil99

Guru

Joined: 11/02/2018
Location: Australia
Posts: 3044
Posted: 01:44am 14 Sep 2025
Copy link to clipboard 
Print this post

You may be able to use a digital out/open collector pin to switch the range via another resistor in the lower leg of the divider and have the best of both worlds.

When the ADC value exceeds a suitable limit set the pin low.
When the ADC value falls below a limit determined the ratio of the two ranges set the pin high.

Your software could then either adjust the display to suit the range, or for maximum resolution on the low range, just change the trace colour to show when it is on the high range.
 
KeepIS

Guru

Joined: 13/10/2014
Location: Australia
Posts: 2062
Posted: 02:03am 14 Sep 2025
Copy link to clipboard 
Print this post

Hi Phil, good idea and that would be easy to do as well, but luckily I put a big information header in the code file for various Hall Sensor sizes in the Series that I use.

I realized that all I had to do was to swap the 400A sensor for a 500A sensor and change a code define. The full scale sensor output voltage stays the same, but the Amperes per volt changes, with the 500A sensor my Limit is now 100A higher.

That is still not enough for the really big startup loads but should cover my normal household running loads, hopefully!


NANO:Inverter V 8.2ksLinux AvrDude GUI script V3.3
 
KeepIS

Guru

Joined: 13/10/2014
Location: Australia
Posts: 2062
Posted: 10:18pm 17 Sep 2025
Copy link to clipboard 
Print this post

With the higher current sensor installed we peaked at a little over 13kW AC at 7am this morning, mainly resistive loads.

Similar high load levels for short periods (10 minutes) in the evenings, then sits at around 4kW to 8kW for 30 to 50 minutes before dropping to under 1kW after cooking and showers are finished, under 400 watts after 9PM.
_
Edited 2025-09-21 11:07 by KeepIS
NANO:Inverter V 8.2ksLinux AvrDude GUI script V3.3
 
KeepIS

Guru

Joined: 13/10/2014
Location: Australia
Posts: 2062
Posted: 02:16am 01 Dec 2025
Copy link to clipboard 
Print this post

I uploaded updated Hex file which have only one change.

The change allows you to use a simple Terminal program with minimal terminal options.

The only change in the Code effects the Terminal application transmit CR-LF setting, when say, TeraTerm terminal APP is connected to the Nano Inverter for accessing the Nano settings Menu:

IE. Windows TeraTerm should now be set to:

Transmit New-Line set to CR  (was LF)

Receive New-Line stays at LF, no change. 

I find a lot of Linux terminals are either totally stupid for a simple interface to talk to a simple micro with text interface, hence the change, I really should have done this right from the start.

The best simple and clean Linux terminal that I have found is GtkTerm:

In the GtkTerm Configuration Menu:

Tick "Local Echo".

Click Port, be sure to scroll the port selection box right to the end, a number of /dev/ttyS0, ttyS1, ttyS2 etc ports are shown in the list, it does not mean they actually exist, Linux MX, Zorin and Ubuntu etc, all show the Nano USB port as the last entry being /dev/ttyUSB0 in each case.

Set Buad Rate: 57600, Bits: 8, Stopbits 1, Flow none, Parity: none.

In Control Signals Menu: Select Open Port (or press F5)

In View Menu set ASCII.

Once it's all going, select "save configuration" from the Configuration Menu.

NOTE : Do not select "Autoreconnect" in the Configuration Menu:

I found a problem when the program loads and does not find the port at startup, it seems to trash the config file and won't run after that causing a permission denied error, you may not have that problem, but there is really no need to have this option in any case.

Really nice simple little terminal for talking to t he Nano controller.
.
Edited 2025-12-01 18:46 by KeepIS
NANO:Inverter V 8.2ksLinux AvrDude GUI script V3.3
 
KeepIS

Guru

Joined: 13/10/2014
Location: Australia
Posts: 2062
Posted: 05:10am 02 Feb 2026
Copy link to clipboard 
Print this post

FYI update: It was in May 2023 that I finished building the first Wiseguy Power board,  it replaced a big China power board in first my DIY Inverter, that WG PWR board has been running since then.

It transferred into the Dual Inverter when it was built around March 2024, I had a spare V1 board which became the second board in the Dual stage INV. I kept the later tested V2 & V3 boards I built for the Dual inverter as backups.
 
I don't know how much power has passed through it, but it ran a year as a single Inverter before I finished the Dual inverter, we used over 4.5 mWh running 24/7 in the past 5 months.

That is climbing faster now as the property, home and workshop are fully electric and everything has now been running 100% off grid. The Nano controller-Inverter has been 100% reliable.
.
NANO:Inverter V 8.2ksLinux AvrDude GUI script V3.3
 
KeepIS

Guru

Joined: 13/10/2014
Location: Australia
Posts: 2062
Posted: 06:12am 20 Feb 2026
Copy link to clipboard 
Print this post

We recently went through 4 days of bleak rainy weather, no sun and very low solar at around 120 W/m2, constant full cloud cover, the 1st day was stinking hot and humid right through the night, and the humidity held over the 4 days.  

At around 6pm the Inverter Tripped?

It had been running at around 12kW for almost 1 hour, I won't bore you with the loads but it was a perfect storm of sustained usage due to the weather conditions and time of day, and the shed door being open.

The shed was warm, someone left the door right next to the Inverter unlatched, as the shed Aircon is at the other end of the shed, it had no cool air, the Toroids were at 59° for the first time ever, that's not a problem at all for them, except someone had set the Toroid over temp trip at 55° I have now set them to 65°.

So we had a 10 minute trip to Mains, and then back to the Inverter.

The Auto Transfer switch in the Main fuse box switched 12kW without issue, when it switched back to the Inverter it dumped a load of 8.7kW back onto the Inverter, I had momentarily switched the Hot water system off for the transfer, no issue at all.

The great news is that we went 4 full days of atrocious solar and weather conditions and the lowest battery charge SOC was at 48%.

FYI: I added a Linux GUI script download to my Sig below. It's for the avrdude command line programmer when using a USBasp device. It's nothing flash (no pun), but it makes uploading Hex files simple. Should anyone try it, I would be interested in hearing if it worked for you, or not. There is some info included with the Script, also included is the avrdude program for Linux. It can also load .hex files from Adruino IDE sketch folders.
NANO:Inverter V 8.2ksLinux AvrDude GUI script V3.3
 
analog8484
Senior Member

Joined: 11/11/2021
Location: United States
Posts: 193
Posted: 05:10pm 20 Feb 2026
Copy link to clipboard 
Print this post

  KeepIS said  
The shed was warm, someone left the door right next to the Inverter unlatched, as the shed Aircon is at the other end of the shed, it had no cool air, the Toroids were at 59° for the first time ever, that's not a problem at all for them, except someone had set the Toroid over temp trip at 55° I have now set them to 65°.


At 59° what's the temp rise against ambient temp?  Was it < 20°?  If so, that's great for 12kW after an hour.

Even 65° seems kinda low.  What is that in terms of the target temp rise vs ambient temp?


On a different topic, given the other thread on the EG8010 frequency issues, how often do you need to adjust appliance clocks with your inverter?
 
KeepIS

Guru

Joined: 13/10/2014
Location: Australia
Posts: 2062
Posted: 10:45pm 20 Feb 2026
Copy link to clipboard 
Print this post

There are so many variables, environmental, toroid physical size, toroid enclosure design and size, toroid mounting position and method, toroid construction, winding layout and cable size, circulating airflow path through and around and over the  toroid, ambient air movement and forced airflow rates around the toroid, and at what point (x temp) forced air flow rate starts.

Then the heat soak temp in the core over time due to the previous average running power level over x time, and before that substantial increase in power levels over time. Finally, where are the measurement sensors taking the readings, unless you place a sensor deep inside the toroid metal core, then you have to ask, how much of that heat is radiated cable heat, verses, the actual slow increase in real internal core heat, which has a massive hysteresis for temperature change due to the shear bulk size and weight of the these stacked cores.

Keep in mind the need to allow for the skin effect in the primary winding, when attempting to calculate power generated in that winding and the proximity of the primary to the sensors.

The hint would be in my case, I can reduce measured toroid temperature quite quickly, a few minutes of forced air needed, once the 12kW power level drops, I have designed an extremely efficient air flow path system that flows air Through, over and around, including over the bottom of each 3 stack toroid xformer.

This indicates that although the sensors are mounted between the stacked cores, and against the core, between the primary windings (covered not touching), most of the heat is likely cable radiated heat and core surface area temperature increases from same.

Mains sync time Clocks:
Adjust about 3 minutes every 2 or 3 weeks. Fortunately it's a few second adjustment for the microwave and oven. The night time security lights around the property run from a central timer and only get adjusted every 6 months, if I remember or notice the drift.


BTW: I've uploaded a new version of the Linux GUI script, allows more options in the .ini file.  
:
Edited 2026-02-21 12:25 by KeepIS
NANO:Inverter V 8.2ksLinux AvrDude GUI script V3.3
 
analog8484
Senior Member

Joined: 11/11/2021
Location: United States
Posts: 193
Posted: 05:59pm 21 Feb 2026
Copy link to clipboard 
Print this post

I forgot you have very good active cooling setup so the transformer temp should stay low even under high load.  Nice to see it in action.
 
KeepIS

Guru

Joined: 13/10/2014
Location: Australia
Posts: 2062
Posted: 08:56am 23 Feb 2026
Copy link to clipboard 
Print this post

  analog8484 said  At 59° what's the temp rise against ambient temp? Was it < 20°? If so, that's great for 12kW after an hour.

Even 65° seems kinda low. What is that in terms of the target temp rise vs ambient temp?


I forgot to answer your question, ambient was around 35°c, the Toroid measurement was around 40°c before it went to 59°c @ 12kW, where it held for almost 1 hour. The heatsinks on the back of the cabinet have no forced cooling, just convection air flow, they got to around 42°c each.

The results from this is that both Toroids and both power stage heatsinks, tracked each other and reached the same temperatures at the same time, so everything is still nicely balanced.

It makes you realise just how much power running at a sustained 12kW output really takes, and it tests every component in the system, it's not something a poor connection or weak point anywhere is going to survive, or a small cramped enclosed housing with a smaller toroid and poor airflow.

In winter it wasn't a problem, but the weather and conditions we had over the 4 days would have been unbearable without the Air conditioners. We had 3 of our 4 Rev-Cycle Inverter-Aircons running for 24 hours a day over that time, it was ridiculously oppressive with very high humidity all through the night, of course we were fine at around 25°c with minimal humidity, but just stepping outside felt like walking into a hot oven
.
Edited 2026-02-23 18:57 by KeepIS
NANO:Inverter V 8.2ksLinux AvrDude GUI script V3.3
 
analog8484
Senior Member

Joined: 11/11/2021
Location: United States
Posts: 193
Posted: 05:08pm 28 Feb 2026
Copy link to clipboard 
Print this post

  KeepIS said  
I forgot to answer your question, ambient was around 35°c, the Toroid measurement was around 40°c before it went to 59°c @ 12kW, where it held for almost 1 hour. The heatsinks on the back of the cabinet have no forced cooling, just convection air flow, they got to around 42°c each.
.


Wow, that's quit low heatsink temp at 12kW after an hour without fan cooling.  IIRC, the heatsinks are quite large though.  I wonder what the inverter efficiency is at 12kW.
 